160 cfm for 4 x4 x 6.7 tent
#355112 - 01/29/10 09:28 PM (15 years, 1 month ago) |
|
|
I got a 4 inch ecoplus inline rated at 160, will it be adequate for my tent. 400w setup.
be peaceful.
|
DrGreenThumb



Registered: 08/09/08
Posts: 487
Loc: Phish Tour
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: psycle]
#355321 - 01/30/10 05:33 AM (15 years, 1 month ago) |
|
|
Yes, that should be just about ideal for the space and light you are working with.
-------------------- “Be who you are and say what you feel because those who mind don't matter and those who matter don't mind.” -Dr. Seuss
|
coda


Registered: 04/20/08
Posts: 4,736
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: DrGreenThumb]
#355475 - 01/30/10 02:02 PM (15 years, 1 month ago) |
|
|
You might be able to get away with it as long as you have a nice supply of cool air getting into your room. A 250 would be a bit better because you'll be able to exchange the air almost twice a minute at that rating.
--------------------
MFDoom666: sobriety kills my buzz every time.
|
psycle
Stranger


Registered: 12/20/09
Posts: 77
Last seen: 14 years, 6 months
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: coda]
#356103 - 01/31/10 06:17 PM (15 years, 1 month ago) |
|
|
http://www.amazon.com/gp/product/B002V9PBXO/ref=oss_product
this is the tent i got, i already ordered it and just started reading about toxic tents, im assuming this one is not toxic, as it says "non toxic" but im just checkin. cant put my girls in a toxic environment, that would be sad man.
|
Inverted
CNC Machinist/Greenthumb



Registered: 06/01/08
Posts: 9,953
Loc: North Star
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: psycle]
#356992 - 02/02/10 08:51 PM (15 years, 1 month ago) |
|
|
If you are talking feet, then it works out like this.
107 Ft3
160CFM
160 divided by 107 = 1.49
That means that your system will be able to exchange the volume of air inside your cab 11/2x/Minute, which is just about right.
1 cycle per minute is generally considered as the Standard/Minimum, and 2x per minute is thought to be Ideal, so at 1.5x I'd say you are going to be just fine. Just make sure your passive intake vents are large enough to not restrict airflow.
How are you setting this up, are you just using a cooltube/reflector to cool the space or are you using a Passive system?
-------------------- Don't criticize what you can't understand
|
psycle
Stranger


Registered: 12/20/09
Posts: 77
Last seen: 14 years, 6 months
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: Inverted]
#357018 - 02/02/10 09:43 PM (15 years, 1 month ago) |
|
|
i was just going to mount the fan right at the exhaust vent with the c/filter attached straight to it.
|
Inverted
CNC Machinist/Greenthumb



Registered: 06/01/08
Posts: 9,953
Loc: North Star
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: psycle]
#357023 - 02/02/10 09:45 PM (15 years, 1 month ago) |
|
|
As an outtake fan right?
So you should have some passive intake vents at the bottom I would assume then?
You should take some pictures of it, or did you not get it yet?
-------------------- Don't criticize what you can't understand
|
psycle
Stranger


Registered: 12/20/09
Posts: 77
Last seen: 14 years, 6 months
|
Re: 160 cfm for 4 x4 x 6.7 tent [Re: Inverted]
#357316 - 02/03/10 06:30 PM (15 years, 1 month ago) |
|
|
yah it just came in today i'll take some pics here in a while, ya it does have an intake.
|
|